Arctica Chiller Static Test


limsc
 Share

Recommended Posts

  • SRC Member

Did anyone tried this Arctica troubleshooting guide Static Test before? BTW, 60F = 15.6degC

Can share with me.. I am still troubleshooting if my chiller is functioning properly.

Mine too ~25mins instead of the stated 5mins.

THANKS if anyone can take the trouble to test his arctica. My is a 1/5HP.

Static Test

Performing a Static Test will allow the chiller to operate without any external factors such as heat

load from equipment, volume load of water capacity, or pump water flow. The main purpose of

this test is to establish that the controller, relay, fan motor, compressor, and temp probe are in

working order without being linked to the actual tank set up.

Step 1

Turn off the pump that flows through the chiller

This test only requires the small amount of water already within the heat exchanger.

Step 2

Program the controller to 60F for the set point

Press the up or down arrow and hold until the number starts to blink, then release and press the

down arrow until the temperature on the controller reads 60F and then release. It will blink and

then the temperature will show a solid color. It is now set to 60F; it will take approximately 5

minutes or less for a functioning chiller to bring the temp down to 60F due to the small amount of

water volume in the heat exchanger.

Link to comment
Share on other sites

  • SRC Member

Hi, i followed your steps and the following were my observations:-

19 11 hrs : Displayed temp on the chiller was 28.9, lowered to 16.5; Chiller kicked in almost immediately

19 16 hrs : Displayed temp on the chiller was 22.2

19 21 hrs : Displayed temp on the chiller was 15.5, Chiller stopped.

by the way, chiller is about 5-6 months old

Link to comment
Share on other sites

  • SRC Member

Hi, i followed your steps and the following were my observations:-

19 11 hrs : Displayed temp on the chiller was 28.9, lowered to 16.5; Chiller kicked in almost immediately

19 16 hrs : Displayed temp on the chiller was 22.2

19 21 hrs : Displayed temp on the chiller was 15.5, Chiller stopped.

by the way, chiller is about 5-6 months old

Thanks triggerfish.. so yours took 10mins..

Look like in Spore weather <5min is unachievable.. but mine still a bit too long whopping 25mins. (maybe my room too warm)

Any more brothers to confirm this observations??

BTW, what capacity is your chiller.. mine is 1/5HP

Link to comment
Share on other sites

  • SRC Member

Thanks triggerfish.. so yours took 10mins..

Look like in Spore weather <5min is unachievable.. but mine still a bit too long whopping 25mins. (maybe my room too warm)

Any more brothers to confirm this observations??

BTW, what capacity is your chiller.. mine is 1/5HP

mine is 1/5 HP too. but mine is placed outside the cabinet, near the main door which is always left open for ventilation etc.

Link to comment
Share on other sites

  • SRC Member

Thanks triggerfish.. so yours took 10mins..

Look like in Spore weather <5min is unachievable.. but mine still a bit too long whopping 25mins. (maybe my room too warm)

Any more brothers to confirm this observations??

BTW, what capacity is your chiller.. mine is 1/5HP

mine is 1/5 HP too. but mine is placed outside the cabinet, near the main door which is always left open for ventilation etc.

Tested it again.. within 10mins.. :whistle "Phew"

Maybe that day when i tested, the room was still warm, probably after the chiller just turn off..

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share



×
×
  • Create New...