why always blackout


pokmingsheng
 Share

Recommended Posts

  • SRC Member

my house seem to have a problem with blackouts..

i'm not sure when, but it started some time back..

every few days, on one faithful night, it'll blackout..

there were even times where it blackout 3days in a row,

and wierdly, each time it happens around 1am..

changed the electric box,

technician couldnt figure out why..

still happens..

anyone can advice?

each time we call a tech to drop by to check,

he couldnt figure out why, and we still have to pay him.. =/

could it be:

power overload? (4rooms running aircon everynight)

my 2ft cube consuming too much electricity? (cant be right)

My Decomissioned 2ft Cube: (31st March 2011)

Carpe Diem~!!!

My Current 4ft X 2ft X 2ft:

Link to comment
Share on other sites

  • SRC Member

just your unit?

If a man could beat his own fantasy. Then to only breed in captivity. Then its pointless.

Genesis 1:20

And God said, Let the waters bring forth abundantly the moving creature that has life, and fowl that may fly above the earth in the open firmament of heaven. And God created great whales, and every living creature that moves, which the waters brought forth abundantly, after their kind, and every winged fowl after his kind: and God saw that it was good. And God blessed them, saying, Be fruitful, and multiply, and fill the waters in the seas, and let fowl multiply in the earth. And the evening and the morning were the fifth day.

|| Tank: 78" x 30" x 30" || Sump: 48" x 22" x 20" || Lights: PowerModule 10 X 80W|| Returns: 2 x HF32 ||

|| Skimmer: BubbleKing Supermarin 300 || Wavemaker: 3 x 6100 & 1 x 6200, 2 x Wavebox 6212, WavySea ||

|| FR: 2 x FR150 || NR: Sulphur Denitrator || CR: RM Custom Made 8" || KR: Deltec KM500 || TopUp: Tunze Osmolator 3155 ||

|| UV: Coralife 12X 36W || Ozonizer: Sanders C200|| Controller: GHL Profilux Plus II Ex ||

Link to comment
Share on other sites

  • SRC Member

just your unit?

yes..

doesnt happen to others..

my mum kept saying because of high electricity consumption,

but i believe those staying in big houses/exec would have a higher consumption..

i'm staying in a 5room flat..

and the blackout occurs when most of the lights are off..

only my tank pumps are running,

air cons in the rooms are running..

and maybe sometimes the TV... =/

My Decomissioned 2ft Cube: (31st March 2011)

Carpe Diem~!!!

My Current 4ft X 2ft X 2ft:

Link to comment
Share on other sites

  • SRC Member

yes..

doesnt happen to others..

my mum kept saying because of high electricity consumption,

but i believe those staying in big houses/exec would have a higher consumption..

i'm staying in a 5room flat..

and the blackout occurs when most of the lights are off..

only my tank pumps are running,

air cons in the rooms are running..

and maybe sometimes the TV... =/

maybe its the aircon since it happened mostly at night. but i could be wrong. check any faulty appliance around. hope you find the source soon enough. all the best.

If a man could beat his own fantasy. Then to only breed in captivity. Then its pointless.

Genesis 1:20

And God said, Let the waters bring forth abundantly the moving creature that has life, and fowl that may fly above the earth in the open firmament of heaven. And God created great whales, and every living creature that moves, which the waters brought forth abundantly, after their kind, and every winged fowl after his kind: and God saw that it was good. And God blessed them, saying, Be fruitful, and multiply, and fill the waters in the seas, and let fowl multiply in the earth. And the evening and the morning were the fifth day.

|| Tank: 78" x 30" x 30" || Sump: 48" x 22" x 20" || Lights: PowerModule 10 X 80W|| Returns: 2 x HF32 ||

|| Skimmer: BubbleKing Supermarin 300 || Wavemaker: 3 x 6100 & 1 x 6200, 2 x Wavebox 6212, WavySea ||

|| FR: 2 x FR150 || NR: Sulphur Denitrator || CR: RM Custom Made 8" || KR: Deltec KM500 || TopUp: Tunze Osmolator 3155 ||

|| UV: Coralife 12X 36W || Ozonizer: Sanders C200|| Controller: GHL Profilux Plus II Ex ||

Link to comment
Share on other sites

some suggestions:

Does the blackout happens when someone switch on the appliance or lights? or maybe when the fridge or chiller kicks in?

Could be the transient in the electrical lines.

THere is this thing that you plug into your power plug to help suppress these transients and also "clean" up spikes in your voltage line.

you might want to see if those help.

The other thing that you want to try is to see if with the blackout still occurs with one or two aircon units switch off.

Sometimes certain applicance (in my experience, a ceiling fan) is already faulty but still can use.

Everything is ok and running even though I switch it on. but after a while, it trips the circuit board.

The hardest part is that it is intermittent.

Maybe you want to try isolating some of the appliance and try to locate which one over time.

When it black out, is it the main circuit breaker on the circuit board or the sub circuit breaker (one of the smaller switch on the circuit board.)

If it is the sub, then try to identify which powerpoints are connected to that sub breaker and isolate the appliance to identify which is the culprit.

Good luck bro!

Eqpt: Deltec MCE 600, Tunze 6055 with Tunze 7091 controller, Artica 1/15 HP chiller, AquaIllumination Sol Blue LED Light System

2011 resolution : Do it simpler, better and in an easier way!

Link to comment
Share on other sites

If your main breaker is tripping, you may have an Earth leakage problem. I suspect the aircon to be the culprit. Happen to me at my old house. Kept tripping in the middle of the night.

I doubt its the lights. They don't use that much current.

Try not using the aircon for the time being and see if it trips again.

Link to comment
Share on other sites

  • SRC Member

Did you check your electrical board which breaker trips? The two largest breakers are the MCB (Main Circuit Breakers) which are rated at 40A. These will only trip if the current load is more than the rated current or if there is a short circuit.

The smaller circuit breakers are rated at 32A if I remember correctly and will only trip if the current is more than that or if there is a short circuit.

The Earth Leakage Circuit breaker (ELCB) is the one with the blue switch. This will trip if any of your electric appliances has a leakage current of more than 30mA. This is the only one that will cause your whole house to trip.

If you suspect that your aircon is the culprit, then what you can do is in the daytime, switch on your aircons one by one. If any of your aircons has a leakage current, your ELCB will trip once you switch on that aircon unit.

My Setup:

3x2x2 tank with IOS

Equipment List:

Chiller: Artica 1/5HP

Chiller Pump: Sicce 4000

Return Pump: OR3500

Skimmer: Deltec APF600

Wavemaker: Tunze Wavebox/2x Hydor K2/SCWD wavemaker

Lights: DElighting 2x150W MH + 2x 39W T5 Atinic

FR: Skimz

FR Pump: Atman AT-104

Tubby ATO, Kalkweisser Reactor with magnetic stirrer.

Link to comment
Share on other sites

Did you check your electrical board which breaker trips? The two largest breakers are the MCB (Main Circuit Breakers) which are rated at 40A. These will only trip if the current load is more than the rated current or if there is a short circuit.

The smaller circuit breakers are rated at 32A if I remember correctly and will only trip if the current is more than that or if there is a short circuit.

The Earth Leakage Circuit breaker (ELCB) is the one with the blue switch. This will trip if any of your electric appliances has a leakage current of more than 30mA. This is the only one that will cause your whole house to trip.

If you suspect that your aircon is the culprit, then what you can do is in the daytime, switch on your aircons one by one. If any of your aircons has a leakage current, your ELCB will trip once you switch on that aircon unit.

Kiko,

I think no need to hire electricians lah....

just buy Peter a cup of kopi and ask him to help to isolate the problem :)

Eqpt: Deltec MCE 600, Tunze 6055 with Tunze 7091 controller, Artica 1/15 HP chiller, AquaIllumination Sol Blue LED Light System

2011 resolution : Do it simpler, better and in an easier way!

Link to comment
Share on other sites

  • SRC Member

Hi,

happened to me before and no one seemed to know why. However, when during the air-con maintenance, the men found out that the wires were exposed. hence the problem resolved since then.

suggest that you take a look around those 'hidden places'. hope it helps!

Link to comment
Share on other sites

  • SRC Member

thanks for all the advice!

the next time it trips, i'll try to look at the switches carefully..

all the jargons that you guys are using,

i've to slowly read the posts again.. haha...

the aircon at my place is those portable kind..

one in every room..

so they're each connected to one powerpoint..

that shouldnt be a problem right?

then again,

it could be my chiller.. (2nd hand)

i've to monitor again the next time it trips..

thanks alot once again for the advice guys :)

My Decomissioned 2ft Cube: (31st March 2011)

Carpe Diem~!!!

My Current 4ft X 2ft X 2ft:

Link to comment
Share on other sites

  • SRC Member

Same here, the last time my house kept on tripping @ night was when the aircon was on. It turned out there was a electrical ciruict in my condenser unit was screwed ... so I also suspect it's your air con condenser unit that has some electrical fault because i'm sure your tank stuff is also on during the day but no blackout during the day right? :) Get your air con condensers checked thoroughly. :)

Cheers,

Desi

Cheers, ;)

Desi

Sheldon (TBBT): A little misunderstanding? Galileo and the Pope had a little misunderstanding...

Link to comment
Share on other sites

  • SRC Member

hope there wont be much moisture around the wires in the aircon to mess with.

that if its the aircon's fault.

If a man could beat his own fantasy. Then to only breed in captivity. Then its pointless.

Genesis 1:20

And God said, Let the waters bring forth abundantly the moving creature that has life, and fowl that may fly above the earth in the open firmament of heaven. And God created great whales, and every living creature that moves, which the waters brought forth abundantly, after their kind, and every winged fowl after his kind: and God saw that it was good. And God blessed them, saying, Be fruitful, and multiply, and fill the waters in the seas, and let fowl multiply in the earth. And the evening and the morning were the fifth day.

|| Tank: 78" x 30" x 30" || Sump: 48" x 22" x 20" || Lights: PowerModule 10 X 80W|| Returns: 2 x HF32 ||

|| Skimmer: BubbleKing Supermarin 300 || Wavemaker: 3 x 6100 & 1 x 6200, 2 x Wavebox 6212, WavySea ||

|| FR: 2 x FR150 || NR: Sulphur Denitrator || CR: RM Custom Made 8" || KR: Deltec KM500 || TopUp: Tunze Osmolator 3155 ||

|| UV: Coralife 12X 36W || Ozonizer: Sanders C200|| Controller: GHL Profilux Plus II Ex ||

Link to comment
Share on other sites

  • SRC Member

LOL it is always the air con! My office kept tripping for a few weeks, no electrician could solve it, finally the air-con serviceman found that the condensation in the compressor was shorting some loose wire.

My 1.5ft nano cube

My 24G nano tank (Decommed)

I can picture in my mind a world without war, a world without hate.

And I can picture us attacking that world, because they'd never expect it.

-- Jack Handey

Link to comment
Share on other sites

  • SRC Member

could it be the heater? mine tripped 2 weeks ago and it was the old heater's problem.

God Blessed all who appreciate His wonderful and beautiful creations.

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

my first reef aquarium 15jan2010

3x2x2ft EOS 10mm tank with sump//deltec sc2060 skimmer//arctica 1/10hp chiller

maxpect g2 170w led//vortech mp40w wavemaker//eheim 1262 universal pump

eheim compact+ 3000 chiller pump//caribsea ocean direct live sands 40lbs

and other misc...

Link to comment
Share on other sites

  • SRC Member

Did you check your electrical board which breaker trips? The two largest breakers are the MCB (Main Circuit Breakers) which are rated at 40A. These will only trip if the current load is more than the rated current or if there is a short circuit.

The smaller circuit breakers are rated at 32A if I remember correctly and will only trip if the current is more than that or if there is a short circuit.

The Earth Leakage Circuit breaker (ELCB) is the one with the blue switch. This will trip if any of your electric appliances has a leakage current of more than 30mA. This is the only one that will cause your whole house to trip.

If you suspect that your aircon is the culprit, then what you can do is in the daytime, switch on your aircons one by one. If any of your aircons has a leakage current, your ELCB will trip once you switch on that aircon unit.

whenever it trips,

its never the small circuit breakers..

its always the main circuit breakers..

sometimes, its the circuit board outside my house..

you know HDB flats, they've this meter thing that runs, there's actually a switch above..

we were told to check that if it trips..

i understand that once it trips,

you just have to switch it on, and it'll come on immediately..

but most of the time, the switch would be quite hot..

have to wait a few mins, before we can push the switch up again..

its kinda worrying... esp when no one can do anything abt it..

now that you guys mentioned,

most likely suspect is the aircon..

but it doesnt trip immediately..

the aircon would have been running for about 3-4hrs,

around 1am++ it'll trip..

and wierdly, its always around that time...

i'll wait and see..

another blackout should happen again during the week... :ph34r:

My Decomissioned 2ft Cube: (31st March 2011)

Carpe Diem~!!!

My Current 4ft X 2ft X 2ft:

Link to comment
Share on other sites

sounds like twilight zone... do do do do.... do do do do....

Eqpt: Deltec MCE 600, Tunze 6055 with Tunze 7091 controller, Artica 1/15 HP chiller, AquaIllumination Sol Blue LED Light System

2011 resolution : Do it simpler, better and in an easier way!

Link to comment
Share on other sites

  • SRC Member

most likely suspect is the aircon..

but it doesnt trip immediately..

the aircon would have been running for about 3-4hrs,

around 1am++ it'll trip..

and wierdly, its always around that time...

Switch on, run for a few hours... Condensation builds up, gathering moisture into water droplets... Boomz! Sounds like a good theory, you should check your air con.

My 1.5ft nano cube

My 24G nano tank (Decommed)

I can picture in my mind a world without war, a world without hate.

And I can picture us attacking that world, because they'd never expect it.

-- Jack Handey

Link to comment
Share on other sites

Switch on, run for a few hours... Condensation builds up, gathering moisture into water droplets... Boomz! Sounds like a good theory, you should check your air con.

i kinda suspect that too.

Eqpt: Deltec MCE 600, Tunze 6055 with Tunze 7091 controller, Artica 1/15 HP chiller, AquaIllumination Sol Blue LED Light System

2011 resolution : Do it simpler, better and in an easier way!

Link to comment
Share on other sites

  • SRC Member

99.99% is caused by one of your portable aircons. 0.01% act of god... :eyebrow:

My Setup:

3x2x2 tank with IOS

Equipment List:

Chiller: Artica 1/5HP

Chiller Pump: Sicce 4000

Return Pump: OR3500

Skimmer: Deltec APF600

Wavemaker: Tunze Wavebox/2x Hydor K2/SCWD wavemaker

Lights: DElighting 2x150W MH + 2x 39W T5 Atinic

FR: Skimz

FR Pump: Atman AT-104

Tubby ATO, Kalkweisser Reactor with magnetic stirrer.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share



×
×
  • Create New...