SRC Member MOssrope Posted January 15, 2010 SRC Member Share Posted January 15, 2010 Anybody knows how this thing works or if has a spare to let go or where to get it? My chiller display buttons are not functioning anymore.. the numbers are still there though.. not sure if they can be fixed if i try to open it up. Will these external thermostats controller overwrite the current chiller display thermostats? thanks!.. not too good with chillers :< Quote Brown SPS > Kinder Surprise White SPS = Kinder Surprise after expiry date Assumption killed the dinosaurs, they didnt have test kits. Link to comment Share on other sites More sharing options...
SRC Supporter Harlequinmania Posted January 15, 2010 SRC Supporter Share Posted January 15, 2010 mabye you can state what chiller you are currently using now in order for us to help ? Quote 1000 Gallon Tank in the Hole http://www.sgreefclub.com/forum/topic/120957-1000-gallon-3d-hole-in-the-wall/ Link to comment Share on other sites More sharing options...
SRC Member MOssrope Posted January 15, 2010 Author SRC Member Share Posted January 15, 2010 mabye you can state what chiller you are currently using now in order for us to help ? the one thats down is a resun cl450. Quote Brown SPS > Kinder Surprise White SPS = Kinder Surprise after expiry date Assumption killed the dinosaurs, they didnt have test kits. Link to comment Share on other sites More sharing options...
stevenkoh08 Posted January 15, 2010 Share Posted January 15, 2010 for resun it a common problem for it u may consider to fix a external controller to over write it as replace the main controller bout 150 Quote Link to comment Share on other sites More sharing options...
stevenkoh08 Posted January 15, 2010 Share Posted January 15, 2010 Far East Refrigeration (Pte) Ltd (HQ) 112 Lavender Street #04-00 Far East Refrigeration Building Singapore 338728 Tel: (65)-6293-9733 Fax: (65)-6296-5326, (65)-6292-6451 Email: info@fareastref.com.sg RSP Systems Pte Ltd 112 Lavender Street #04-00 Far East Refrigeration Building, Singapore 338728 Tel: (65)-6297-4880 Fax: (65)-6297-4881 Email: rspsys@pacific.net.sg they got sell and at a rate of less then 2 blue note controller w/probe what u need to add is just buy the three pin plug that'll do. Quote Link to comment Share on other sites More sharing options...
SRC Member MOssrope Posted January 15, 2010 Author SRC Member Share Posted January 15, 2010 Far East Refrigeration (Pte) Ltd (HQ)112 Lavender Street #04-00 Far East Refrigeration Building Singapore 338728 Tel: (65)-6293-9733 Fax: (65)-6296-5326, (65)-6292-6451 Email: info@fareastref.com.sg RSP Systems Pte Ltd 112 Lavender Street #04-00 Far East Refrigeration Building, Singapore 338728 Tel: (65)-6297-4880 Fax: (65)-6297-4881 Email: rspsys@pacific.net.sg they got sell and at a rate of less then 2 blue note controller w/probe what u need to add is just buy the three pin plug that'll do. wow thanks a lot steven. i understand i will have to remove the whole casing to change the probe is that true? seems like along the way to reborn.. WHOSE IN FOR A TRIP! Quote Brown SPS > Kinder Surprise White SPS = Kinder Surprise after expiry date Assumption killed the dinosaurs, they didnt have test kits. Link to comment Share on other sites More sharing options...
Gouldian Posted January 18, 2010 Share Posted January 18, 2010 Hi KY, You don't have to remove and dismantle anything from your current chiller. * Most external controller will be wired between the main power supply and a power supply socket * The chiller will be plug into this power supply socket instead of the main power supply (wall socket) * A probe will be connected to the external controller * When the temperature climbs above the pre-set, the external controller will supply power to the socket and thereby the chiller will start running * When the temperature lowered to the pre-set, the external controller will cut supply to the socket and thereby the chiller stop running Hope that helps. Quote "Reefs, like forests, will only be protected in long term if they are appreciated" Dr. J.E.N. Veron Australian Institute of Marine Science -----------------------------------------------------------------------Member of:UEN: T08SS0098FPlease visit us here: http://www.facebook....uaristSocietySG Facebook Group: http://www.facebook....gid=34281892381 Link to comment Share on other sites More sharing options...
stevenkoh08 Posted January 18, 2010 Share Posted January 18, 2010 Ya wat gouldian said is right but only meant for those which are still working with the existing controller (means once u on ur power of the chiller the compressor still cut on) if urs is not working even u power on then u've to re-wire it Quote Link to comment Share on other sites More sharing options...
SRC Member iskay Posted January 18, 2010 SRC Member Share Posted January 18, 2010 Hi KY, You don't have to remove and dismantle anything from your current chiller. * Most external controller will be wired between the main power supply and a power supply socket * The chiller will be plug into this power supply socket instead of the main power supply (wall socket) * A probe will be connected to the external controller * When the temperature climbs above the pre-set, the external controller will supply power to the socket and thereby the chiller will start running * When the temperature lowered to the pre-set, the external controller will cut supply to the socket and thereby the chiller stop running Hope that helps. Hi Bro Gouldian, Does this type of external controller harms the mechanisms in the chiller? I wondering if the chiller has some 'proper-shut off' mechanism that prolongs the life of the equipment. Cheers, Quote "Be formless... shapeless, like water. If you put water into a cup, it becomes the cup. You put water into a bottle; it becomes the bottle. You put it into a teapot; it becomes the teapot. Water can flow, or it can crash. Be water, my friend..." - Lei Siu Lung (Bruce Lee) Link to comment Share on other sites More sharing options...
RockyBoy Posted January 18, 2010 Share Posted January 18, 2010 Hi Bro Gouldian, Does this type of external controller harms the mechanisms in the chiller? I wondering if the chiller has some 'proper-shut off' mechanism that prolongs the life of the equipment. Cheers, I think it might for certain chillers. Sometimes the chiller will let the fan runs a few more minutes to cool down the compressor further. Quote Member of : UEN: T08SS0098FMASS in Facebook Reefing in LED Link to comment Share on other sites More sharing options...
SRC Member BarraCudaTM Posted January 18, 2010 SRC Member Share Posted January 18, 2010 I think it might for certain chillers. Sometimes the chiller will let the fan runs a few more minutes to cool down the compressor further. Dont think there are such function. The compressor is cooled by the refrigerant itself. If the superheat is properly adjusted, the compressor will cool adequately. The fan is only for cooling the condensing coil and does nothing for the compressor. Quote Link to comment Share on other sites More sharing options...
ogykogy Posted January 18, 2010 Share Posted January 18, 2010 also quite intrested in this product. stevenkoh08 are u using one of this(i mean the place ure recommending)?u've got a pic of it? Quote 2 FEET CUBE REEF DISCO(60cmx60cmx60cm) TOTAL 286 LITERS WITH SUMP LIGHTS:PHAROS LED 90 WATTS WITH WIRELESS CONTROLLER RETURN PUMP:EHEIM 1260CHILLER:HAILEA 150A + EHEIM COMPACT 1000 WITH EXT TEMP CONTROLLERWAVEMAKER:JEBAO WP25REACTOR:TLF PHOSBAN REACTOR 150 WITH EHEIM 600(ROWAPHOS)SKIMMER:H&H S150 WITH AQUABEE 2000/1 MEDIA:BACTERIA KING GLASS CLEANER:ALGAE FREE PIRANHA FLOAT WITH EASY BLADE ATO:TUNZE NANO OSMOLATOR 3152 RO/DI PURIFIER:ZeRO EX5 - RO/DI ULTRA 200 WITH HM DIGITAL DM-1 IN-LINE DUAL TDS METER Link to comment Share on other sites More sharing options...
SRC Member MOssrope Posted January 20, 2010 Author SRC Member Share Posted January 20, 2010 thanks for the input so far is a relay needed to further control the voltage going into to the external controller to prevent it from fusing? or the original wires from the chiller is enough... afraid to connect the wrong ones but its always good to learn... as mentioned in 1st post.. the existing controller has the temp set but i cant adjust it. Power on it turns on.. its set at 18 so it goes on and on and on... i intend to remove the usage of the existing controller totally.. i understand u guys using the wire connected to the female socket is due to the existing controller still in use... do i still need to attach the new external controller to a female socket then plug in the chiller? and yes the addition of a relay too? Quote Brown SPS > Kinder Surprise White SPS = Kinder Surprise after expiry date Assumption killed the dinosaurs, they didnt have test kits. Link to comment Share on other sites More sharing options...
Gouldian Posted January 21, 2010 Share Posted January 21, 2010 Hi KY, * No further relays needed * Plug the external temp controller directly into the wall socket * Set the temperature * Plug the chiller plug into external controller socket If your chiller temperature setting is stuck at lower that desired temperature, the above method will work well without you needed to de-comm the old controller. Quote "Reefs, like forests, will only be protected in long term if they are appreciated" Dr. J.E.N. Veron Australian Institute of Marine Science -----------------------------------------------------------------------Member of:UEN: T08SS0098FPlease visit us here: http://www.facebook....uaristSocietySG Facebook Group: http://www.facebook....gid=34281892381 Link to comment Share on other sites More sharing options...
Gouldian Posted January 21, 2010 Share Posted January 21, 2010 Hi Bro Gouldian, Does this type of external controller harms the mechanisms in the chiller? I wondering if the chiller has some 'proper-shut off' mechanism that prolongs the life of the equipment. Cheers, Hi Stephen, Most sensitive electronics may need "soft start and stop" function to ensure longer life span. But I don't think the chiller electrical wirings and performance may suffer from such overwrite. The part that is likely to be affected with the the chiller temp controller but this is usually redundant once the external controller is in play. Quote "Reefs, like forests, will only be protected in long term if they are appreciated" Dr. J.E.N. Veron Australian Institute of Marine Science -----------------------------------------------------------------------Member of:UEN: T08SS0098FPlease visit us here: http://www.facebook....uaristSocietySG Facebook Group: http://www.facebook....gid=34281892381 Link to comment Share on other sites More sharing options...
SRC Member peacemaker Posted January 21, 2010 SRC Member Share Posted January 21, 2010 I do have one for sale, so if anyone is interested, do PM me for details. Quote Link to comment Share on other sites More sharing options...